Q:Will this breaker fit a PN3048L1200C sub panel? Need to add the main breaker per code
by|May 1, 2024
1 Answer
Answer This Question
A: Yes, this PN3048L1200C can accept MBK200A as the main breaker. See wiring diagram in the link below.
https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Wiring%20Diagram/SIE_WD_LC_PN3048B-L1200-C.pdf
by|May 2, 2024
Q:Will this fit siemens PNW0816L1200TC Panel
by|Dec 28, 2023
1 Answer
Answer This Question
A: Yes, the PNW0816L1200TC will accept MBK150A. Link to wiring diagram for confirmation: https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Wiring%20Diagram/SIE_WD_LC_PNW0816B-L1200TC.pdf
by|Dec 28, 2023
Q:Will this replace the MBK125M to convert a LC2040L1125 to a main breaker?
by|Nov 16, 2023
1 Answer
Answer This Question
A: Can use either MBK125M (Murray - which is technically now obsolete) or MBK125A (Siemens) to convert this unit from MLO to 125amp Main Breaker. See link below to product wiring diagram under "Main Lug / Main Breaker Kits" for approved main breaker kits.
https://cache.industry.siemens.com/dl/files/480/109796480/att_1065539/v1/MUY_WD_LC2040L1125.pdf
by|Nov 17, 2023
Q:Does a mbk200a fit in a sn4040l1200
by|Nov 8, 2023
0 Answer
Answer This Question
Q:Would this fit a square d box
by|Nov 1, 2023
1 Answer
Answer This Question
A: Siemens breakers are not UL approved to be used in another manufacturers equipment.
by|Nov 2, 2023
Q:Will this replace an EQ9483?
by|Oct 13, 2023
1 Answer
Answer This Question
A: Our current offering is MBK200 but we would need to know the load center part# to advise possible options for main breaker replacement or if our current offering will work in your existing load center ~ email picture of your label to productselection.us@siemens.com
by|Oct 13, 2023
Q:Will this fit in a Gould G2440MB1200 ?
by|Sep 21, 2023
1 Answer
Answer This Question
A: No it won't ~ the main breaker part # for that load center is EQ9685 which is obsolete unfortunately, nothing else will work he can try to find it online somewhere or replace the entire load center.
by|Sep 21, 2023
Q:Can this breaker replace current one 60amp in 125 amp Westinghouse GLC 24N? Thank you!
by|Sep 6, 2023
1 Answer
Answer This Question
A: No. This is not approved for use with the old Westinghouse panels. Unfortunately, due to age, we do not have approved replacement main breakers that would be listed for use with the Westinghouse panel.