Q:Is there a tie bar connecting the ground and neutral bus bars?
by|Nov 14, 2017
3 Answers
Answer This Question

A:  There is a bonding screw for that.

by|May 5, 2023
1 found this answer helpful

A:  there will be a green screw in place that needs to be tightened to bond the neutral bus with the ground bus and the container.

by|May 5, 2023
1 found this answer helpful

A:  Yes there is a tie bar that can be removed if the panel is to be used as a sub panel.

by|May 5, 2023
1 found this answer helpful
caret
Q:Will the 1/2 " breaker fit in this box?
by|Sep 27, 2017
1 Answer
Answer This Question

A:  No you can not only full size breaker work

by|May 5, 2023
    caret
    Q:Can you replace the 125 amp main breaker with a 100 amp breaker?
    by|Jun 17, 2017
    4 Answers
    Answer This Question

    A:  Yes you can.

    by|May 5, 2023

    A:  Yes you can reduce the breaker size. However keep in mind that the conductor feeder size is to always be matched in size to the breaker size.

    by|May 4, 2023

    A:  Yes

    by|May 5, 2023

      A:  No. The safety parameters of your system is compromised when this is attempted

      by|May 5, 2023
        caret
        Q:how large is it
        by|Apr 3, 2017
        2 Answers
        Answer This Question

        A:  The dimensions of the product are 14 W x 33.1875 H x 4.625 D inches.

        by|May 4, 2023
          1 found this answer helpful

          A:  33.1875 x 14 x 4.625"

          by|May 5, 2023
          caret
          Q:What size riser pipe is used on a 125 amp outdoor panel.
          by|Nov 14, 2016
          2 Answers
          Answer This Question

          A:  Usually no smaller than 1 1/2 riser to accommodate the wires to each breaker

          by|May 5, 2023

            A:  this panel will accept up to 2.5" pipe size. You can use any size up to that size. The number and size of the conductors that will be run in the conduit dictate the size of he conduit.

            by|May 4, 2023
            caret
            Q:Can I change the Main breaker to 80-amp?
            by|Nov 8, 2016
            0 Answer
            Answer This Question
            caret
            Q:Is this a TLM 2012 panel box? I am trying to find a cover for my fuse box.
            by|Aug 10, 2016
            1 Answer
            Answer This Question

            A:  This is model TM2010CCU2K.

            by|May 3, 2023
              caret
              Q:in what position will the 1/2 inch breakers fit (diagram)
              by|Jul 4, 2016
              0 Answer
              Answer This Question
              caret
              Q:what amp are the breckers that come with box
              by|Apr 7, 2016
              3 Answers
              Answer This Question

              A:  6-each 1-pole 20-Amp. 1-ea 2-pole 30-Amp & 1-each 2-pole 50-Amp

              by|May 5, 2023

              A:  30 amp 40 and 50 with rest being 20

              by|May 5, 2023

                A:  This kit includes 6 THQP120 single-pole 20 Amp circuit breakers, 1 THQP230 2-pole 30 Amp circuit breaker and 1 THQP250 2-pole 50 Amp circuit breaker.

                by|May 3, 2023
                  1 found this answer helpful
                  caret
                  Q:Later on can you change 125 amp into a 200 amp panel
                  by|Feb 4, 2016
                  4 Answers
                  Answer This Question

                  A:  No you can not the panel is only rated for 125 amps now you can get a main lug convertible to main breaker 200 amps and feed it with a 125 amp breaker use a hold down kit on the breaker

                  by|May 3, 2023
                    1 found this answer helpful

                    A:  No!

                    by|Jul 18, 2017
                      1 found this answer helpful

                      A:  No unless you size the feeder correctly first.

                      by|May 5, 2023

                      A:  Not with this panel. Not with out changing entire panel.