Q:Is there a tie bar connecting the ground and neutral bus bars?
by|Nov 14, 2017
3 Answers
Answer This Question
A: There is a bonding screw for that.
by|May 5, 2023
1 found this answer helpful
A: there will be a green screw in place that needs to be tightened to bond the neutral bus with the ground bus and the container.
by|May 5, 2023
1 found this answer helpful
A: Yes there is a tie bar that can be removed if the panel is to be used as a sub panel.
by|May 5, 2023
1 found this answer helpful
Q:Will the 1/2 " breaker fit in this box?
by|Sep 27, 2017
1 Answer
Answer This Question
A: No you can not only full size breaker work
by|May 5, 2023
Q:Can you replace the 125 amp main breaker with a 100 amp breaker?
by|Jun 17, 2017
4 Answers
Answer This Question
A: Yes you can.
by|May 5, 2023
A: Yes you can reduce the breaker size. However keep in mind that the conductor feeder size is to always be matched in size to the breaker size.
by|May 4, 2023
A: Yes
by|May 5, 2023
A: No. The safety parameters of your system is compromised when this is attempted
by|May 5, 2023
Q:how large is it
by|Apr 3, 2017
2 Answers
Answer This Question
A: The dimensions of the product are 14 W x 33.1875 H x 4.625 D inches.
by|May 4, 2023
1 found this answer helpful
A: 33.1875 x 14 x 4.625"
by|May 5, 2023
Q:What size riser pipe is used on a 125 amp outdoor panel.
by|Nov 14, 2016
2 Answers
Answer This Question
A: Usually no smaller than 1 1/2 riser to accommodate the wires to each breaker
by|May 5, 2023
A: this panel will accept up to 2.5" pipe size. You can use any size up to that size. The number and size of the conductors that will be run in the conduit dictate the size of he conduit.
by|May 4, 2023
Q:Can I change the Main breaker to 80-amp?
by|Nov 8, 2016
0 Answer
Answer This Question
Q:Is this a TLM 2012 panel box? I am trying to find a cover for my fuse box.
by|Aug 10, 2016
1 Answer
Answer This Question
A: This is model TM2010CCU2K.
by|May 3, 2023
Q:in what position will the 1/2 inch breakers fit (diagram)
A: This kit includes 6 THQP120 single-pole 20 Amp circuit breakers, 1 THQP230 2-pole 30 Amp circuit breaker and 1 THQP250 2-pole 50 Amp circuit breaker.
by|May 3, 2023
1 found this answer helpful
Q:Later on can you change 125 amp into a 200 amp panel
by|Feb 4, 2016
4 Answers
Answer This Question
A: No you can not the panel is only rated for 125 amps now you can get a main lug convertible to main breaker 200 amps and feed it with a 125 amp breaker use a hold down kit on the breaker
by|May 3, 2023
1 found this answer helpful
A: No!
by|Jul 18, 2017
1 found this answer helpful
A: No unless you size the feeder correctly first.
by|May 5, 2023
A: Not with this panel. Not with out changing entire panel.