Q:is this panel feed through or do I have to buy a kit to go with it
by|Jul 23, 2020
1 Answer
Answer This Question
A: Hello Billy, this meter breaker does not come with feed-through lugs. You can use a BJ2200 as a sub feed breaker or use the BRPSF225 sub feed lug block. Regards, Eaton.
by|Aug 15, 2022
Q:How is the cover attached? Is it hinged?
by|Nov 2, 2019
1 Answer
Answer This Question
A: Hello, the way the cover on this product is attached is by hinges.
Regards, Eaton
by|Jan 17, 2020
Q:Are there knockouts on the left side also?
by|Nov 2, 2019
1 Answer
Answer This Question
A: Hello, for part number MBE2040B200TS there is a knockout on the left and right side. Regards, Eaton.
by|Nov 27, 2019
Q:What is the main bus rating?
by|Oct 2, 2019
1 Answer
Answer This Question
A: The buss is rated at 200 amps.
by|Oct 4, 2019
Q:Only metal front cover pannel which holds meter n lock ring
by|Sep 10, 2019
1 Answer
Answer This Question
A: Hello Corey, the meter socket cover for MB2040B200BTS is part number MBMSCVR2. Regards, Eaton.
by|Sep 18, 2019
Q:Can I buy just the cover for we’re the meter is placed only
by|Sep 10, 2019
1 Answer
Answer This Question
A: Hello Corey, the meter socket cover for MB2040B200BTS is part number MBMSCVR2. Regards, Eaton.
by|Sep 18, 2019
Q:does this product have feed through lugs, for sub feeding a mobile home
by|Apr 20, 2018
1 Answer
Answer This Question
A: Hello Abel,
No, feed through lugs are not included. These can be ordered separately and take up spaces from the distribution section. The appropriate parts BRSF125 / BRSF150 / 3BRSF150 will need to be special ordered. Please reach out to a Home Depot store associate to place a special order.
Regards,
Eaton
by|May 5, 2023
Q:is this outdoor rated?
by|Jul 5, 2017
1 Answer
Answer This Question
A: Hello Fwells,
Thank you for your question. Yes, this panel has a NEMA 3R rating which means it can be used outdoors.
Regards,
Eaton
by|May 4, 2023
Q:does Eaton make a snap in lug kit for this panel to feed out 200 amps
by|Jun 16, 2017
2 Answers
Answer This Question
A: Hello Eastern,
We appreciate your question.
Yes, the BRS225, main and sub-feed lug blocks, can be used on loadcenters 200 or 225 amp rated.
Regards,
Eaton
by|May 4, 2023
A: Are the lugs in the Meter Pan Horn type. That is a req. with NYSEG.
by|May 4, 2023
Q:is this capable of being a feed thru panel
by|Nov 8, 2016
1 Answer
Answer This Question
A: Hello John,
You can use this meter breaker panel to feed-through to a subpanel. You will need to feed your subpanel either with a BR style branch circuit breaker or a sub-feed lug block that plugs onto the bus in this meter breaker. Use BRSF150 lug block for 150A subpanels, and BRSF125 lug block for 125A subpanels.
Regards,
Eaton