Q:Does this work with cutler hammer box?
by|Apr 1, 2021
2 Answers
Answer This Question

A:  Yes, but only the Cutler-Hammer BR series panels and not the Cutler-Hammer CH series panels.

by|Apr 12, 2021
1 found this answer helpful

A:  Yes it does, any BR type. Will not fit CH type.

by|Apr 2, 2021
    caret
    Q:Is this suitable and/or listed for a multiwire branch circuit, one breaker on each circuit with a handle tie? If not, is there an Eaton arc fault or af/gf breaker that’s suitable and/or listed for a multwire branch circuit?
    by|Feb 28, 2021
    1 Answer
    Answer This Question

    A:  What you suggest is not suitable and will not work. When using single pole AFCI breakers each circuit must have a dedicated neutral conductor. However, Eaton does make both Type CH and BR series 2-pole AFCI circuit breakers. The Type BR 2-pole AFCI breaker should work for you.

    by|Mar 4, 2021
    2 found this answer helpful
    caret
    Q:I received a very helpful answer r.e. my 15 amp EATON combination type AFCI type BRAF. Now that I know this is an old version, I need to know if I replace it with this Eaton BR 15 amp breaker or if I need something else. And, if I do need something different, what I need. Thanks in advance
    by|Feb 13, 2021
    1 Answer
    Answer This Question

    A:  If you are sure your older AFCI breaker is bad, replace it with this newer version. The most common complaint with the early version was nuisance trips and the newer technology has all but eliminated those problems. This newer version is a combination AFCI breaker meaning it protects against both parallel and series arcing.

    by|Feb 26, 2021
    1 found this answer helpful
    caret
    Q:I have an 15 amp EATON combination type AFCI type BRAF. Is this BR breaker an acceptable replacement or do I need to find a BRAF breaker?
    by|Feb 13, 2021
    2 Answers
    Answer This Question

    A:  Type BRAF is the early generation of Eaton AFCI breakers so if that is what you have, you DO NOT have the combination type AFCI breaker. The combination type AFCI breaker is this one which is a Type BRCAF. The older Type BRAF version is no longer available.

    by|Jul 4, 2022
    2 found this answer helpful

    A:  Thanks for the help on this. Knowing I have an old version that is not available, I need to know if I replace it with this BR breaker of ? Thanks!

    by|Jul 4, 2022
      caret
      Q:please recommend a store available replacement for the AFCI/GFCI (blue label) pictured. Thanks
      by|Mar 14, 2020
      1 Answer
      Answer This Question

      A:  Your old yellow label BRAF were a first generation AFCI breaker that has been replaced with the newest generation Combination AFCI circuit breakers. The Combination type protects against both series and parallel arcing where the first generation only protected against parallel arcing. The blue label breakers in your picture are of the dual function AFCI/GFCI type and are rarely needed. Unless you specifically need the GFCI protection on those circuits I'd replace them with Combination AFCI breakers. All are available in stock at almost all HD stores.

      by|Jan 10, 2024
      4 found this answer helpful
      caret
      Q:Hi is this the same as the Type BRAF with the yellow lable
      by|Feb 14, 2020
      1 Answer
      Answer This Question

      A:  No, it isn't the same. The BRAF was from the first generation of arc fault breakers where this is a BRCAF which is the latest generation and replaces the older BRAF. This latest generation is a combination arc fault breaker which means it protects against both parallel and series arc faults. The BRAF only protected against parallel arc faults.

      by|Dec 12, 2022
      6 found this answer helpful
      caret
      Q:how many circuits can this have
      by|Jan 18, 2020
      2 Answers
      Answer This Question

      A:  One at 120V at 20 Amps... The wire you attach to it should be a 12AWG, that number can be found with good eyes or a magnifying glass on the wire itself... If you have a 14AWG to hook up, you need to buy the 15 Amp version

      by|Jan 20, 2020
      1 found this answer helpful

      A:  This arc fault breaker is for one 20 amp 120 volt circuit.

      by|Apr 12, 2021
      2 found this answer helpful
      caret
      Q:Is the GFCI test button on a working three-prong plugin outlet tester able to verify that the GFCI function on this circuit breaker actually works? The test button on the circuit breaker itself trips it, but two outlet testers in parallel (both are 18K ohms, 6.7mA, verified with an ohmmeter and an ammeter, 13.3 mA total) do NOT trip it. My vague understanding is that a residential GFCI should trip at 5mA. I get the same behavior on 4 different branches with similar BR20 AFCI circuit breakers on them (installed 8 years apart). Each outlet tester does trip other outlets with built-in GFCI, and other branches with older GFCI breakers on them (one of them connected to the same neutral bar in the 200A electrical panel).
      by|Jan 15, 2020
      3 Answers
      Answer This Question

      A:  This is an arc fault circuit interrupting circuit breaker that does not perform a ground fault function. I would not expect a plug-in receptacle tester with a GFCI test button to trip any AFCI circuit breaker.

      by|Apr 12, 2021
      3 found this answer helpful

      A:  Thank you TomB2 for your prompt and informative answer. I tested a spare AFCI "Combination" breaker with a desktop experiment: a 120V isolation transformer, a couple of DVMs, and a few different resistors. A 5.1K ohm resistor from hot output to neutral input doesn't trip it, a 4.7K ohm resistor will, so a ground fault of more than 24 mA is required to trip this AFCI Combination breaker. Next, I will learn about which branches ought to have Dual breakers instead of AFCI Combination breakers, both for maximum safety and future code compliance. Thanks again.

      by|Apr 12, 2021

        A:  Yes, the tester creates a ground fault, so unless the tester is no good the GFCI should trip, if it doesn't try other GFCIs to verify your tester is good, and return the bad GFCI as defective... I have an old tester that has a permanent ground fault, simply plugging it in trips the circuit...

        by|Apr 12, 2021
        caret
        Q:Can I install this AFCI in an almost 30 year old Westinghouse load center. (I understand Eaton absorbed Westinghouse some time back, at least the part that makes breakers.)
        by|Sep 26, 2019
        2 Answers
        Answer This Question

        A:  Keep in mind this is an arch fault and not a ground fault that said depending on the amount this may work for you.

        by|Feb 13, 2021

        A:  Yes, this is the correct AFCI breaker for your Westinghouse loadcenter.

        by|Feb 13, 2021
        7 found this answer helpful
        caret
        Q:Is this product compatible with Westinghouse . Westinghouse Panel catalog no. B20 3040CT I am replacing a Westinghouse BR 15 at breaker to a arc fault. Thank you
        by|Jun 27, 2019
        1 Answer
        Answer This Question

        A:  Yes, this is the correct arc fault breaker for your Westinghouse panel.

        by|Feb 13, 2021
        8 found this answer helpful

        Frequently Bought Together

        +
        +
        Price:
        $37.35

        Compare Similar Items

        current item

        Breaker Type

        Single Pole

        Single Pole

        Main Breaker

        Main Breaker

        Interruption Type

        CAFCI

        AFCI

        AFCI/GFCI

        AFCI/GFCI

        Mounting Type

        Plug-On

        Plug-On

        Plug-On

        Plug-On

        Series Type

        BR

        BR

        BR

        CH

        Connection Type

        Pigtail

        Pigtail

        Neutral

        Neutral