Q:Will this fit a wadsworth panel
by|Sep 27, 2023
1 Answer
Answer This Question

A:  Wadsworth did not use Zinsco style breakers. The UBIA line of breakers are the Wadsworth style replacement breakers.

by|Sep 28, 2023
    caret
    Q:Do the stores carry the parts say here?s the whole panel
    by|Jul 13, 2023
    1 Answer
    Answer This Question

    A:  Store availability varies by location and you would have to contact them directly for specific inventory. Online through the website is generally the simplest way to purchase the items.

    by|Jul 14, 2023
      caret
      Q:What's the difference between this item and this other breaker? https://www.homedepot.com/p/Connecticut-Electric-New-VPKUBIZ-Thin-15-15-Amp-3-4-in-1-Pole-Zinsco-Twin-R3815-Replacement-Circuit-Breaker-VPKUBIZ1515/100056356
      by|Aug 5, 2022
      1 Answer
      Answer This Question

      A:  The only difference is in the packaging. The VPK versions are packaged in a sealed plastic clamshell for storefronts while the non-VPK versions are just the breaker by itself. The actual circuit breaker is the same for both SKUs but Home Depot stocks both and often sets their own price.

      by|Mar 17, 2023
        1 found this answer helpful
        caret
        Q:ARE ZINSCO BREAKERS RATED FOR aluminum WIRE
        by|Mar 21, 2019
        2 Answers
        Answer This Question

        A:  Yes they are CU-AL rated.

        by|Apr 22, 2019
          1 found this answer helpful

          A:  Yes, Zinsco breakers have been frequently used with aluminum wire since the mid 1960s. Many of those houses that haven't burned down still have Zinsco breakers.

          by|Apr 22, 2019
          caret
          Q:If the busbars are damage can the be repaired without changing out the entire box?
          by|Apr 7, 2017
          2 Answers
          Answer This Question

          A:  The bus bars in your Zinsco panel (or Zinsco style Sylvania panel) are tin plated aluminum. If they are damaged it's because they are burnt. Zinsco panels are known for this and are also a known fire hazard. Any attempted repair would just be temporary. You really should be replacing the panel soon.

          by|Apr 22, 2019
          1 found this answer helpful

          A:  Usually not and better long term repair to replace the box.

          by|May 6, 2020
            caret
            Q:I am looking to replace a burned out Zinsco circuit breaker (Type RC38AL) 40degrees C. Will this be the correct replacement - Zinsco 30 Amp 3/4 in. Duplex Single-Pole Type Z UBI Replacement Circuit Breaker
            by|Mar 8, 2017
            1 Answer
            Answer This Question

            A:  This breaker might fit your panel, but I want to caution you to inspect the aluminum busbars carefully, many times they are damaged when the old breaker burns up. The issue with Zinsco usually is the contact between the breaker and the busbars which permanently damages the aluminum busbars. Another issue is that this is a 30 amp tandem single pole breaker. The NEC limits 120 volt single pole circuits for lighting and receptacles to no more than 20 amps. You probably should be looking for a 20 amp tandem single pole breaker. You probably should start a fund to replace that obsolete panel, it is obsolete for good reason.

            by|Apr 22, 2019
            1 found this answer helpful
            caret
            Q:Zinsco panels & breakers are documented fire hazard and were recalled - does this breaker remedy this?
            by|Sep 20, 2016
            2 Answers
            Answer This Question

            A:  No, this breaker does not remedy the fire issue with Zinsco panels, it is merely a replacement for a bad breaker.

            by|Apr 22, 2019
            1 found this answer helpful

            A:  No it does not, I had a short in a wire and the zinsco breaker burned a hole in it and never tripped.

            by|Nov 11, 2021
              caret
              Q:Is this double pole 3/4 inch thick
              by|Dec 29, 2015
              1 Answer
              Answer This Question

              A:  This breaker is 3/4" thick, but it isn't a double pole. This is a tandem single pole breaker. It provides two 30A, 120 volt circuits in a single 3/4" space.

              by|Apr 22, 2019
              2 found this answer helpful

              Frequently Bought Together

              +
              +
              Price:
              $78.92

              Compare Similar Items

              current item

              Breaker Type

              Tandem

              Double Pole

              Double Pole

              Double Pole

              Interruption Type

              Standard Trip

              Standard Trip

              Standard Trip

              Standard Trip

              Mounting Type

              Plug-On

              Plug-On

              Plug-On

              Plug-On

              Pack Size

              1

              1

              1

              1

              Power Distribution Features

              Trip Indicator

              No Additional Features

              No Additional Features

              No Additional Features