#1 Home Improvement Retailer

Questions and Answers for Square D 7 Terminal Ground Bar Kit for QO/Homeline Electrical Panel/Load Center(PK7GTACP)

Internet #202353316

Model #PK7GTACP

Store SKU #578169

  • 7 terminal Ground Bar Kit for use in Square D electrical panels
  • Accepts copper or aluminum wire to feed to neutral bar
  • UL listed and ANSI Certified

Questions & Answers

62Questions
caret
Q:how do I separate ground and neutral terminations in a subpanel in a boathouse? A square D GFCI breaker in Main Panel immediately defaults to ground with both N and G on same subpal bar, How additional PK3GTA bar need to be insulated from the subpanel?
by|Mar 18, 2023
2 Answers
Answer This Question

A:  The neutral in a subpanel should be isolated from ground. If you install a PK3GTA on the backplane of the panel and land your conductor grounds there, this should solve your problem. Remove any neutral bonding jumper to ground.

by|Jun 25, 2023
    3 found this answer helpful

    A:  Hi, Below the FAQ to know how neutral is bonded QO and HOM. https://www.se.com/us/en/faqs/FA100207/ Regards, Schneider Electric Customer Care

    by|Mar 28, 2023
      caret
      Q:Will two of the 23 position ground bars fit end to end on one side of a Homeline 200 amp panel?
      by|Dec 28, 2022
      2 Answers
      Answer This Question

      A:  If this is a main panel, there is a bonding screw that connects neutral to ground near the main breaker. If your neutral and ground are bonded, there is not a need for a ground bar. all grounds and neutrals can land on the neutral bars.

      by|Jul 6, 2023
        1 found this answer helpful

        A:  Hi, In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

        by|Jul 28, 2023
          caret
          Q:Will this accept #3 copper wire?
          by|Dec 11, 2022
          1 Answer
          Answer This Question

          A:  Hello Daryl, No, the PK7GTACP won't accept #3 CU wire. The CU wire size it accepts is : (1) #14-#4 or (2) #14 or #12. Regards, Schneider Electric Customer Care

          by|Apr 6, 2023
            caret
            Q:Since these are aluminum, does one need that electrical grease to connect to a copper wire?
            by|Nov 25, 2022
            1 Answer
            Answer This Question

            A:  Hi, The use of an antioxidant on the load centers main lugs is not required. The lugs are UL listed for use with copper or aluminum conductors without the use of any antioxidation supplement. The use of an antioxidant is not prohibited, but assure that the brand used is a NON-PETROLEUM based product. If a petroleum based product is used, and comes in contact with the insulating base, it can degrade the insulating base material. Regards, Schneider Electric Customer Care

            by|Oct 22, 2023
              1 found this answer helpful
              caret
              Q:What size are the screws to mount ground bar to sub panel
              by|Oct 21, 2022
              2 Answers
              Answer This Question

              A:  The ground bar should come with the screws to attach it to the panel can, if not 8/32 screws.

              by|Oct 22, 2022

                A:  Hi, There are different mounting screws for different, for PK23GTACP mounting screws are 21594-14220 (8-32 X 0.68in - two required). http://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/313000/FA313449/en_US/PK%20ground%20bar%20data%20from%20LC%20catalog.pdf

                by|Oct 1, 2023
                  caret
                  Q:Are screws to attach to the bar to box included?
                  by|Sep 8, 2022
                  2 Answers
                  Answer This Question

                  A:  Yes

                  by|Sep 11, 2022

                    A:  Hi, Ye,the ground bar includes the mounting screws. Regards, Schneider Electric Customer Care

                    by|Sep 8, 2022
                      caret
                      Q:How does this attach to the box?
                      by|Aug 28, 2022
                      1 Answer
                      Answer This Question

                      A:  Hi, Below the instruction bulletin: https://download.schneider-electric.com/files?p_enDocType=Instruction+sheet&p_File_Name=40272-070-02.pdf&p_Doc_Ref=40272-070-02 Regards, Schneider Electric Customer Care

                      by|May 7, 2023
                        1 found this answer helpful
                        caret
                        Q:Can this bus bar be used with neutral wire and ground wire and hot wire
                        by|Jul 31, 2022
                        1 Answer
                        Answer This Question

                        A:  Hi, Unfortunately no, this is only tested to be grounded bar. Regards, Schneider Electric Customer Care

                        by|Aug 1, 2022
                          caret
                          Q:How many #12 wires can be connected to this ground bar?
                          by|May 1, 2022
                          2 Answers
                          Answer This Question

                          A:  I'm not sure what the manufacturer suggest, but I would say 2 #12 wires per terminal slot seems ideal. If this is a 15 terminal bar, then 30 #12 wires total.

                          by|Jun 7, 2023
                            1 found this answer helpful

                            A:  Hello Eweneek1, This PK15GTACP comes with 15 slots. Regards, Schneider Electric Customer Care

                            by|May 3, 2022
                              caret
                              Q:With 7 holes, why would it not accommodate (2) #8 wires and more #12 or #10 wires?
                              by|Apr 21, 2022
                              3 Answers
                              Answer This Question

                              A:  Dave, In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

                              by|Apr 22, 2022

                                A:  In separate holes, it definitely would. Just not two #8 conductors in the same hole.

                                by|Jun 18, 2023

                                  A:  You can purchase different sizes for different needs

                                  by|Jul 20, 2022

                                  Frequently Bought Together

                                  +
                                  +
                                  Price:
                                  $8.35