Questions and Answers for Murray 60 Amp 2-Space 4-Circuit Main Lug Surface Mount Load Center

Internet #202253181

Model #LC002GS

  • Murray brand is being phased out, replaced by equal Siemens parts
  • Murray LC002GS is equivalent to Siemens E0204ML1060S
  • HS type Hub Provision Only

Questions & Answers

21Questions
caret
Q:What wire & breaker size do I need to connect this to main panel?
by|Jan 9, 2021
1 Answer
Answer This Question

A:  LC006NSU is a main lug load center. It is simply the Murray-labeled version of E0816ML1125S. Please refer to wiring diagram link. #4 to 2/0 AWG Cu or Al is accepted. If backfeeding a main breaker please observe the wire range listed on the breaker label. Main breaker size would depend on application needs. https://www.downloads.siemens.com/download-center/Download.aspx?pos=download&fct=getasset&id1=BTLV_42727

by|Jan 14, 2021
    caret
    Q:I'm trying to find some quad breakers for this panel, but can't seem to find any that fit. I'm looking for a 2-pole 20amp and 2-pole 30 amp quad breaker and a 2-pole 20 amp and 2-pole 30 amp breaker. Any recommendations for breakers that will fit?
    by|Dec 1, 2020
    1 Answer
    Answer This Question

    A:  The quad breakers are Murray type MH-T breaker which are approved for use in the LC008DSU load centers. 2p20/2p30a would be part# MP220230CT2 which is available via Home Depot's website as well. The 2 inside poles of the quadplex breaker will be the 2p20a and the outside poles will be the 2p30a. Standard 2p 20a breaker would be part# MP220U. Standard 2p 30a breaker would be part# MP230U. The Siemens breakers would also be interchangeable with these. MP220230CT2: closest Siemens Q23020CT2 (30a inner poles and 20a outer poles), MP220U = Siemens Q220U, MP230U = Siemens Q230U.

    by|Dec 3, 2020
      caret
      Q:Does this box accept standard seimens/GE breakers?
      by|Sep 24, 2020
      1 Answer
      Answer This Question

      A:  GE breakers are not approved for use in LC002GS. Murray Type MP-T and now also Siemens Type QP breakers are. For a copy of the UL substitution letter authorizing Siemens-labeled breakers please send a request to productselection.us@siemens.com.

      by|Sep 24, 2020
        caret
        Q:What is the size of this box?
        by|Apr 3, 2020
        1 Answer
        Answer This Question

        A:  LC002GS is 9-7/8" H x 5-1/8" W x 2-5/8" D.

        by|Apr 3, 2020
          caret
          Q:Can I use this to supply two 220v loads?
          by|Mar 28, 2020
          2 Answers
          Answer This Question

          A:  Yes, with a Murray Type MH-T Quadplex or Siemens Type QT Quadplex breaker installed (MP215215CT2 or Q21515CT2, for example for dual 15A). A UL substitution letter is available for Siemens in place of Murray. Send a request to productselection.us@siemens.com for a copy.

          by|Mar 30, 2020

            A:  I would buy a bigger box, code requires two spares.

            by|Mar 28, 2020
            caret
            Q:I have a distance of 25Ft from my main panel what size wire should I use to connect this box?
            by|Jun 21, 2019
            1 Answer
            Answer This Question

            A:  LC002GS is the Murray labeled version of E0204ML1060S. Line terminal lugs accept #14 to #2 AWG wire. Please consult with a licensed electrician for the proper wire size for your application in compliance with the NEC. For cut sheet and wiring diagram information please go to the link below and select "Downloads" and enter E0204ML1060S in the search box. https://w3.usa.siemens.com/powerdistribution/us/en/Pages/low-medium-voltage.aspx

            by|Jun 25, 2019
              caret
              Q:Will this accept Murray type MH-T circuit breakers?
              by|Aug 24, 2018
              1 Answer
              Answer This Question

              A:  Yes Murray MH-T is a UL approved branch type for LC008DSU.

              by|May 6, 2023
                caret
                Q:Do I need to buy a ground bar for the panel?
                by|Aug 19, 2018
                1 Answer
                Answer This Question

                A:  LC008DSU does not included a factory installed ground bar. Equipment Ground Bars: Catalog No. Series "LX" can be field added. For reference, LC008DSG does include a factory installed ground bar.

                by|May 5, 2023