Questions and Answers for Lithonia Lighting 4 in. GU10 Brushed Nickel Glass Shower Recessed Kit-DISCONTINUED

Internet #202512355

Model #LK4LBN U

Questions & Answers

7Questions
caret
Q:Are these lights IC rated?
by|Jan 28, 2016
1 Answer
Answer This Question

A:  No. You must maintain and minimum of 3" of clearance all the way around the fixture.

by|May 3, 2023
    caret
    Q:This is called a shower kit but the Q & A on others from Lithonia are only damp rated is this one?
    by|Mar 1, 2014
    1 Answer
    Answer This Question

    A:  This kit includes a lensed trim that is appropriate for wet locations. Thanks for your question.

    by|May 3, 2023
      1 found this answer helpful
      caret
      Q:Do these dim well?
      by|Feb 24, 2014
      1 Answer
      Answer This Question

      A:  Yes, with a standard incandescent wall box dimmer. Thanks for your question.

      by|May 3, 2023
        caret
        Q:Will this light fit into an opening that is exactly 4 inches?
        by|Oct 13, 2013
        1 Answer
        Answer This Question

        A:  Hi JoeM, you need a hole that is 4 & 1/8 inches. You're so close, try sanding around the hole to increase the size just enough to have the light fit. The hole should be round. If it's square you can enlarge, however you should fill in the area where there is space around the light.

        by|May 2, 2023
        caret
        Q:Can this light be installled in a T&G ceiling, even though the wood is combustable?
        by|Oct 20, 2012
        1 Answer
        Answer This Question

        A:  Yes it can. UL states that contact points for installation at the front rim and where clips connect, as well, is permissible. The only hindrance may be the ceiling thickness. The clips are designed for standard 5/8” thick sheet rock as a maximum. Thank you!

        by|May 2, 2023
          caret
          Q:I have blown in insulation in my ceiling. If I clear it away at least 3 in. from the housing, can I install the light even though it is non-ic?
          by|Oct 20, 2012
          1 Answer
          Answer This Question

          A:  Yes, but the insulation does need to be moved (especially off the top of the cans since most of the heat dissipates from the top). You may need to check from time to time to make sure it hasn’t shifted around and deposited on the unit. Thank you!

          by|May 2, 2023
            caret
            Q:Insulation
            by|Sep 9, 2012
            1 Answer
            Answer This Question

            A:  Yes, it can.

            by|May 2, 2023