Questions and Answers for GE Q-Line 30 Amp 1 in. Double-Pole Circuit Breaker

Internet #100356518

Model #THQP230

Store SKU #198285

  • Q-line plug-in breaker for residential load centers
  • Internal common trip bar and box type terminals
  • Quick make, quick break switch

Questions & Answers

77Questions
caret
Q:Can I use this breaker to run my fridge and dishwasher separately
by|May 15, 2023
2 Answers
Answer This Question

A:  No. Each leg of this breaker is 40 amps. You need two breakers of the appropriate sizes for your appliances.

by|Feb 22, 2024

    A:  Yes, you can use this 2-pole breaker for a 20A multiwire branch circuit which means both circuits share the neutral conductor. Use 12-3 NM cable.

    by|Mar 18, 2024
      caret
      Q:I have a 2" 30 amp double pole breaker for a Dryer circuit. I'm looking to save space in the panel. Would this 1" breaker be the equivalent to what I have? My current breaker type is BR230 if that helps.
      by|Apr 8, 2023
      2 Answers
      Answer This Question

      A:  Thanks for the question. Your part number indicates you have an Eaton panel. You would need to check their offering to see what is available.

      by|Apr 15, 2023

        A:  No, this GE breaker cannot be used in a Cutler-Hammer panel.

        by|Mar 18, 2024
          caret
          Q:Will this work with a Callenger breaker box?
          by|Mar 21, 2023
          2 Answers
          Answer This Question

          A:  No, THQP breakers will only fit SOME GE panels.

          by|Mar 18, 2024

            A:  Thanks for the question. GE does not recommend using GE breakers in any other brand of load centers nor other brands of breakers in GE load centers.

            by|Jul 6, 2023
              caret
              Q:can ge 20 amp breaker. accept 2 awg wire
              by|Mar 9, 2023
              2 Answers
              Answer This Question

              A:  The THQL2120 is designed for 20 amps, and accepts 12 to 8 awg wire. Thank you for your question.

              by|Mar 10, 2023

                A:  No, it will not accept #2s.

                by|Mar 18, 2024
                  caret
                  Q:What are the torqueing specs for the 15, 20 and 30 amp Q-Line breakers from GE
                  by|Nov 28, 2022
                  2 Answers
                  Answer This Question

                  A:  Listed as 1 2 and 3 pole 10 to 30 amp 34lb-in(4)N-m 40 to 60 amp 45lb-in(5) N-m

                  by|Nov 4, 2023

                    A:  Torque specs are on the label on the breaker.

                    by|Mar 19, 2024
                      caret
                      Q:I need to replace a double pole breaker that GE has labeled with the "20" on each pole. These new breakers only says "20" on one pole. Does that mean my old breaker is 40amp? or did GE just change the way they are labeled? Picture of old amp attached.
                      by|Oct 18, 2022
                      3 Answers
                      Answer This Question

                      A:  Your old breaker is probably a 20A THQL, a different breaker than this THQP.

                      by|Mar 18, 2024

                        A:  they just changed the labeling

                        by|Mar 13, 2023

                          A:  Thanks for the question. What you have is a 2 pole 20 amp breaker. Thanks

                          by|Feb 4, 2024
                            3 found this answer helpful
                            caret
                            Q:Will this breaker work in tl412r1p panel?
                            by|Sep 25, 2022
                            2 Answers
                            Answer This Question

                            A:  Hello - to better answer your question, please contact our HD.com customer service department at 800-430-3376 any day between 6 a.m. and 2 a.m. EST, or call your local store. They can either answer your question or transfer you to your local store to answer your specific question. -- We hope to hear from you soon. Take care. - Pablo@GEA

                            by|Sep 28, 2022

                              A:  Check the label inside the panel cover to see what type breakers the panel will accept. Look for THQP.

                              by|Mar 18, 2024
                                caret
                                Q:Are these 25 amps per pole and 50 amps total for 240v?
                                by|Jun 29, 2022
                                3 Answers
                                Answer This Question

                                A:  Hi! Thanks for reaching out. To better answer your question, please contact our HD.com customer service department at 800-430-3376 any day between 6 a.m. and 2 a.m. EST, or call your local store. They can either answer your question or transfer you to your local store to answer your specific question. Best wishes. -Michael@GEA

                                by|Nov 30, 2023

                                  A:  Let me try an explain it in a simple way. The double pole breaker that saids 50 amp is 50 amp per pole. So 50 amps per wire. You never add the them, so it's not 25 plus 25 to give you 50 amp, it's 50 amps per side aka pole.

                                  by|Jan 28, 2024
                                    5 found this answer helpful

                                    A:  If the breaker is marked "50" it is 50 amps per pole for a total of 50 amps at 240 volts.

                                    by|Mar 18, 2024
                                      caret
                                      Q:Can I use 2 of these to replace an existing 2-inch dual pole 30A breaker (see picture) to have one more 240V circuit? I suppose I have to move the 1/2" in position 10 to position 2 then install 2 of these in positions 4 and 8. Is that correct? Thanks!
                                      by|Apr 30, 2022
                                      5 Answers
                                      Answer This Question

                                      A:  While this is possible you should actually buy a quad breaker that ties the outer and inner breakers together. It should be noted that some panels are not compatible with mini and quad breakers to prevent them from being overloaded however if your panel already has other mini-breakers it should work. When you buy the quad you can get a 30 matched with the other size your installing but make sure the wire is large enough for the breaker otherwise it could cause a fire (Example: 14awg = 15 amp, 12awg = 20 amp, 10awg = 30amp).

                                      by|May 4, 2022

                                        A:  Hire a licensed electrician and don't burn the house down. You'll also need rewiring work done.

                                        by|Jan 17, 2023
                                          1 found this answer helpful

                                          A:  Two of these THQP breaker may not fit in the space of one THQL breaker. Consult the bus layout on the label inside the panel.

                                          by|Mar 18, 2024

                                            A:  Location is important! On this dual pole breaker, there is a tab which sticks out at the back; it fits into a little curve in the bar behind the breakers. The breaker must span two slots (the B of 4 and A of 6) to not fry your appliance.

                                            by|Jun 27, 2023

                                              A:  #1 You have to make sure you have a load center that accepts 1/2" frame breakers in all positions. I will say our panels feature a rejection feature that won't allow you to plug on a breaker that is not designed to be placed in that position. #2 If you are unsure please hire an electrician to assist. Thanks

                                              by|May 19, 2022
                                                1 found this answer helpful
                                                caret
                                                Q:Breaker box model- GE # TL412C We have bought 2 of these and the flange on the bottom of the breaker does not fit into our box. We broke off that tab but then it only worked as 2 120 volts not together as a 240. Is there another model# I should try?
                                                by|Feb 3, 2022
                                                4 Answers
                                                Answer This Question

                                                A:  I am assuming this breaker box is for single phase 120/240 Volt service? If it is the box is set up so that every other slot is an alternate leg of 120 Volts.. As you know in order to get 240 Volts you need to plug this breaker in so that it plugs into an opposing leg of 120 Volts. Typically if you look at the panel and start from the very top of the bus on either side of the panel you will notice that the slots are numbered. Typically if you start on the left side of the panel and work your way down, the first two slots should be numbered 1 and 3. and you should only be able to plug a double pole breaker in these slots. If you try to plug the breaker into slots 3 and 5 (This would be slot directly below slot 3) for example the breaker should not fit and even if it did you would only be getting 120Volts since the power would be coming from the same leg. Finally, it is also possible that this breaker is not designed for your GE panel so check the model number of the box and go to the GE website to determine if the breaker you are using can be used in that particular panel box. I hope this helps and if you have any doubts about what you are doing contact a licensed electrician. Finally, since you broke the tabs off of the breaker, be sure to discard it as it is now trash.

                                                by|Jan 27, 2024
                                                  3 found this answer helpful

                                                  A:  Thank you chick! You saved me a bunch of troubleshooting. Why does this panel come with a double pole 30amp slimline breaker which is limited on which spots it can go in...but then does not say so anywhere like inside the panel would be great...

                                                  by|Oct 12, 2022

                                                    A:  These do not fit in the same as full size breakers. If you start at the top of a panel and count down on the left it goes 1,3,5,7…, The same on the right except even numbers. In order for this breaker to be 240 volt it must be installed in spaces 3 and 5 or 4 and 6. Then you follow same pattern going down. It always starts on B phase. 

                                                    by|Nov 22, 2022
                                                      2 found this answer helpful

                                                      A:  First, check the label inside the panel to see if type THQP breakers can be used. If you find it listed, check the bus layout to see where they can be used.

                                                      by|Mar 18, 2024

                                                        Frequently Bought Together

                                                        +
                                                        +
                                                        Price:
                                                        $15.48

                                                        Compare Similar Items

                                                        current item

                                                        Breaker Type

                                                        Double Pole

                                                        Standard

                                                        Double Pole

                                                        Double Pole

                                                        Interruption Type

                                                        Standard Trip

                                                        Standard Trip

                                                        Standard Trip

                                                        Standard Trip

                                                        Mounting Type

                                                        Plug-On

                                                        Plug-On

                                                        Plug-On

                                                        Plug-On

                                                        Series Type

                                                        Not Specified

                                                        Homeline

                                                        Not Specified

                                                        Not Specified

                                                        Connection Type

                                                        Non-Neutral

                                                        Non-Neutral

                                                        Non-Neutral

                                                        Non-Neutral