Q:What's the difference between the thick double pole 30amp and a thin double pole 30amp circuit breaker? Can I use either one just the same and it'll be ok for an electric dryer?
by|Mar 12, 2024
2 Answers
Answer This Question

A:  The THQP230 performs the same application as the THQL2130 but in half of the space required, but can only be installed in GE load centers that accept THQP space saving breakers. Thank you for your question.

by|Mar 13, 2024

    A:  Both the thick and thin are for 240 volt circuits. The Thin THQP breakers can only be used in some GE loadcenters. Beware though, the thin THQP breakers used in older GE aluminum bus loadcenters have been known to catch on fire when heavily loaded.

    by|Mar 18, 2024
      caret
      Q:Will this work in an old challenger panel?
      by|Nov 14, 2023
      1 Answer
      Answer This Question

      A:  No, GE Type THQP breakers will not fit any panel except some GE panels.

      by|Mar 18, 2024
        caret
        Q:Will this 50amp 1? breaker accept 6awg wire?
        by|Sep 9, 2023
        3 Answers
        Answer This Question

        A:  GE's THQP 1- & 2-pole breakers only fit GE panels that can accommodate them. Check your panel's directory decal, which also shows bus bar configuration. If it indicates A and B on some positions (e.g. 25A, 25B, 28A, 28B, etc.), then THQP can be used.

        by|Dec 13, 2023
          1 found this answer helpful

          A:  Yes, it will accept #6 wire which is necessary for a 50 amp circuit when using NM cable. Only #8 is required for 50A circuits if the conductors are THHN in conduit.

          by|Mar 18, 2024

            A:  some brain surgeon needing to rewrite the electrical code whenever they turn him loose has now deemed the number 8awg is no longer fit for a 50 amp breaker. Forcing the industry to rewire 100's of 50 amp house appliances to number #6 wire.

            by|Jan 25, 2024
              caret
              Q:im having a ev charger installed that puts out 32 amps that uses an nema 1450 outlet that electrician is installing, before i buy the charger will this 40 amp breaker fit in by ge panel box its 200 amp panel box
              by|Aug 12, 2023
              1 Answer
              Answer This Question

              A:  Read the label inside the panel, it will tell you what breakers can be used in your panel. Look for type THQP. Follow the installation instructions for the amperage of the breaker.

              by|Mar 18, 2024
                caret
                Q:Does this put out 220 v , 110 on each pole?
                by|Aug 8, 2023
                3 Answers
                Answer This Question

                A:  This breaker functions the same as any other 2-pole breaker. It's not a tandem breaker. It only fits GE panels in spaces that can accommodate THQP breakers. Being 2-pole it must be installed on the half stabs of adjoining spaces (e.g. 26B & 28A, etc.)

                by|Nov 11, 2023

                  A:  The breaker does not put out voltage. You draw current through the breaker. This breaker is typically used for 240 volt circuits.

                  by|Mar 18, 2024

                    A:  No. Both poles are on the same phase.

                    by|Dec 1, 2023
                      2 found this answer helpful
                      caret
                      Q:I?m installing a receptacle to run a small 110/220 welder (50amp). Will the 1? split breaker work for that or should I move a breaker and go with the 2?.
                      by|Jun 25, 2023
                      1 Answer
                      Answer This Question

                      A:  This type THQP 2-pole breaker will give you 240 volts.

                      by|Mar 18, 2024
                        caret
                        Q:Can I use this breaker to run an electric stove
                        by|Jun 10, 2023
                        2 Answers
                        Answer This Question

                        A:  You stove will have the minimum breaker specification. Be sure to follow those specs. Also make sure the wiring gage is appropriate for the load. Lastly, to be honest. If you have to ask that question I would strongly recommend you hire a licensed electrician to help you. You will be able to sleep at night knowing that your house will not burn down. 

                        by|Nov 18, 2023
                          2 found this answer helpful

                          A:  No, this is just a 20 amp breaker. Most electric ranges require a 40 amp circuit and some require a 50 amp circuit. Check the manufacturer's installation instructions.

                          by|Mar 18, 2024
                            caret
                            Q:Will this breaker fit in a TM2015 breaker box
                            by|Jun 7, 2023
                            1 Answer
                            Answer This Question

                            A:  Check the label inside the panel for the breaker types the panel will accept. Look for type THQP.

                            by|Mar 18, 2024

                              Frequently Bought Together

                              +
                              +
                              Price:
                              $16.31

                              Compare Similar Items

                              current item

                              Breaker Type

                              Double Pole

                              Double Pole

                              Double Pole

                              Double Pole

                              Interruption Type

                              Standard Trip

                              Standard Trip

                              Standard Trip

                              Standard Trip

                              Mounting Type

                              Plug-On

                              Plug-On

                              Plug-On

                              Plug-On

                              Pack Size

                              1

                              1

                              1

                              1

                              Power Distribution Features

                              No Additional Features

                              No Additional Features

                              No Additional Features

                              No Additional Features