Questions & Answers

134Questions
caret
Q:Will this GE Q line double pole 70 amp breaker accept number 3 AWG wire?
by|Jul 16, 2023
1 Answer
Answer This Question

A:  Thanks for the question. Yes this breaker accepts #6-1/0 CU and #4 - 1/0 AL.

by|Nov 6, 2023
    1 found this answer helpful
    caret
    Q:Will this work on a Siemens Q-Type 200 amp main breaker box?
    by|Jun 19, 2023
    2 Answers
    Answer This Question

    A:  You mean in the main breaker position? Probably not. A Siemens 200a breaker is a lot bigger physically.  But the 125 should plug into the branch circuit bussbars ok. 

    by|Jun 19, 2023

      A:  I just noticed this is a GE breaker. It’s probably not UL listed for use in a Siemens panel. Nit recommended. 

      by|Jul 21, 2023
        caret
        Q:Can you backfeed through this breaker using it as a main
        by|Jun 17, 2023
        2 Answers
        Answer This Question

        A:  Yes

        by|Apr 30, 2024
          1 found this answer helpful

          A:  yes . but it is not recommended

          by|Apr 30, 2024
            2 found this answer helpful
            caret
            Q:Will this breaker accept a 3/0 wire?
            by|May 1, 2023
            1 Answer
            Answer This Question

            A:  No don?t even try

            by|Jun 6, 2023
              caret
              Q:will this breaker fit a crouse hinds cabinet
              by|Apr 3, 2023
              2 Answers
              Answer This Question

              A:  It might.

              by|Apr 9, 2023

                A:  Greta Question! A GE breaker is only UL approved for use in a GE panel.

                by|Apr 4, 2023
                  caret
                  Q:What is torque rating of 2 pole 50 amp breaker
                  by|Feb 23, 2023
                  1 Answer
                  Answer This Question

                  A:  The torque value will be written on the breaker itself.

                  by|Jun 20, 2023
                    caret
                    Q:Will this 125A double pole circuit breaker fit into 2 slots of a GE Powermark plus 200A circuit breaker box?
                    by|Feb 4, 2023
                    2 Answers
                    Answer This Question

                    A:  Absolutely it will. Thanks for the question.

                    by|Feb 4, 2023

                      A:  Maybe. Some 200a panels have a 100a maximum for branch-circuit breakers. Generally you need to look at the manufacturers specs on the piece of paper glued to the panel cover door and see what model of breakers can be installed in that panel. If the 125a is listed there you’re good to go. 

                      by|Feb 10, 2023
                        caret
                        Q:What size of wire do I need for a 60 amp breaker
                        by|Feb 3, 2023
                        2 Answers
                        Answer This Question

                        A:  You can use 6awg wire in a 60amp breaker they say, but I was recommended to use a 4awg wire as I was setting it up for the new hot tub I bought. We were running it underground from the garage to the tub in a PVC conduit. It's been working awesome for a year and a half now.

                        by|Feb 5, 2023

                          A:  according to nec electrical code 60amp can be run on #6 copper wire or #4 aluminum cable

                          by|Aug 14, 2023
                            caret
                            Q:Can I use two of these 100 amp 2 pole to replace a 200 amp 4 pole main breaker
                            by|Jan 10, 2023
                            1 Answer
                            Answer This Question

                            A:  Nope

                            by|Jan 13, 2023
                              caret
                              Q:Will this fit a cutler hammer breaker box?
                              by|Dec 16, 2022
                              5 Answers
                              Answer This Question

                              A:  No, this is only for GE panel You would need an Eaton CH breaker

                              by|Dec 23, 2022

                                A:  This breaker is not UL approved for use in other manufacturer's brands except GE. Thanks for the question.

                                by|Dec 17, 2022

                                  A:  GE circuit breakers are only designed to be used in GE circuit breaker panels 

                                  by|Dec 20, 2022

                                    A:  GE breakers are not listed for use in Cutler Hammer load centers or panels.

                                    by|Nov 2, 2023
                                      1 found this answer helpful

                                      A:  Only the new style, but it is not allowed by code. Breakers should only be installed in manufacturer specific panels.

                                      by|Dec 20, 2022

                                        Frequently Bought Together

                                        +
                                        +
                                        Price:
                                        $74.00

                                        Compare Similar Items

                                        current item

                                        Breaker Type

                                        Double Pole

                                        Triple Pole

                                        Double Pole

                                        Double Pole

                                        Interruption Type

                                        Standard Trip

                                        Standard Trip

                                        GFCI

                                        GFCI

                                        Mounting Type

                                        Plug-On

                                        Plug-On

                                        Plug-On

                                        Plug-On

                                        Series Type

                                        Not Specified

                                        Not Specified

                                        Not Specified

                                        Not Specified

                                        Connection Type

                                        Non-Neutral

                                        Non-Neutral

                                        Pigtail

                                        Pigtail